rongudlin said:
At 125% I get 24,000va divided by 240v would give me a cal load of 100amperes.Is that a safe way to calculate a load to size a feeder ampacity for 16 circuits????
Sounds good from my side of the keyboard. Couple of other sugggestions:
1. Bullrails (plug-in racks) are usually located way out. Watch the voltage drop. If you can, you may wish to locate the xfm and panel out at the rail.
2. If energy use is an issue, look at adding thermostats, timer, and a contactor feeding a dedicated panel. For example:
Turn on at 30F, 1/2 hour on - 1/2 hour off
Turn on solid at -20F
3. If you do use a contactor and a dedicated panel out at the rail, consider adding a second small panel for area lights and a few un-switched receptacles. An amazing phenomenon of nature: Areas that get cold also get dark:wink:
3. GFIs: I don't think gfis are required (but I don't know that). However, a lot commercial users have them. Some use receptacles, others use CBs. If you end up with gfcis, look for a way to know the receptacles are energized. If nothing else, use lighted cords. Amazing as it sounds, that pesky equipment has a way of occasionally knocking out a gfi.
carl