16 KW generator feeder conductors

Status
Not open for further replies.

rojay

Senior Member
Location
Chicago,IL USA
On a 16 KW generator where the nameplate states the rated maximum continuous load current is 66.6 amps- is there any exception that would allow #6 wire to be used for the feeder?
The generator has a 70amp breaker for overload protection and #6 wire could be fused at 70 amps but isn’t the max load current rating the deal breaker here requiring #4 conductors?
 
The only scenario where I think 6awg could be permitted is if all the terminals it's connected to were rated for 90C. That is almost certain to not be the case.
 
You can always run #4 at each end for 3' or more, then cut over to #6 using a 90 degree rated connection means for the long run.

Sent from my XT1585 using Tapatalk
 
You can always run #4 at each end for 3' or more, then cut over to #6 using a 90 degree rated connection means for the long run.

Sent from my XT1585 using Tapatalk

Just because you can doesn't really mean you should. The cost of the splices (probably Polaris connectors) j-boxes, and labor could pay for a lot of #4 wire.

This sounds like a residential application; the cost difference between #6 and #4 wire has to be negligible at this scale.