Looking to feed a 120/208 3 phase switch gear.
Looking at 310.15(B)(16) it looks as though 750s @ 75* are good for 475 amps. 475x4= 1900, 1900x80% per 310.15(B)(3)(a) is 1520amps.
I really can't see going over 750s, is there any provision for allowing a 500, or at least a 600 in this application?
I know I can't use the next size up OCPD per 240.3(C) but this seems excessive.
Thoughts?