F Frost Electric Member Jun 3, 2022 #1 I have a 1600 amp service that called for 4 - 4" runs with 750 AL. I know 750 is good for 385 amps on the 75%. Is this possible?
I have a 1600 amp service that called for 4 - 4" runs with 750 AL. I know 750 is good for 385 amps on the 75%. Is this possible?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jun 3, 2022 #2 Possible! What Code cycle and MLO or Main ??
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jun 3, 2022 #4 In that case 230.90(A) will require 1600 amps of conductor, and you do not have that. There is no rounding up when the OCPD exceeds 800 amps.
In that case 230.90(A) will require 1600 amps of conductor, and you do not have that. There is no rounding up when the OCPD exceeds 800 amps.