I have a 1600A 480V Breaker in a Control Cabinet that powers a Chiller. A few years ago Carrier replaced components in the chiller to correct the tripping issue, but it has persisted. The building has multiples and it has not crippled them, but they want answers.
I was asked to investigate:
The Plastic Fin on the Line side Shroud was burnt and melting on the C-Phase side of the lugs, with les discoloration on the B-Phase (Middle). But the Breaker Tripped on the Load Side of the Lugs, not the Main up stream.
The breaker was swapped out and tested, the New (used) Breaker also tripped and old one passed NETA testing and was re-terminated. all connections have been checked for tightness.
I installed an logging meter on Line and Load and found no issues on all three phases, yet the breaker tripped at around 750A, about 2 hours after start up.
The Thermal Scope shows a temp of about 174deg F. on the lugs.
I noticed the 1/2 of Output wires to the Chiller pass between A-Phase and B-Phase, should this be causing a magnetic/heat issue - ultimately tripping the breaker?
Pic - Chiller 6
I was asked to investigate:
The Plastic Fin on the Line side Shroud was burnt and melting on the C-Phase side of the lugs, with les discoloration on the B-Phase (Middle). But the Breaker Tripped on the Load Side of the Lugs, not the Main up stream.
The breaker was swapped out and tested, the New (used) Breaker also tripped and old one passed NETA testing and was re-terminated. all connections have been checked for tightness.
I installed an logging meter on Line and Load and found no issues on all three phases, yet the breaker tripped at around 750A, about 2 hours after start up.
The Thermal Scope shows a temp of about 174deg F. on the lugs.
I noticed the 1/2 of Output wires to the Chiller pass between A-Phase and B-Phase, should this be causing a magnetic/heat issue - ultimately tripping the breaker?