This system will be installed in a heated garage in a electrical room under the 20 unit Condo complex. I've done this before in the engineering company I worked at and they signed off. It does seem a little strange when you look at it and I've even had one engineer from Canada say they couldn't, (or wouldn't) do it, but the only place in the code is 300.20 A & B that I can find anywhere that talks about the only reason you can't is because of heat effect, if you watch out for that your fine.... you can also use an insulated wall barrier instead of cutting the slots. It's really nice when your using big wire and landing them into a tight place. Also many manufacturing plants have been done this when you run your PVC under the floor and up into switchgear, I've had no problems with it. I would really like to use 5 - 500kcmil but the limitation with the 4 hole connection at the breaker forces me to up the wire size, so I will most likely criss-cross them and go done a wire size. The parallel argument always comes up when someone does the one phase system and I would like to here some more thoughts on it. I've seen it done quite a few times but it isn't the normal way you think about it when you see it for the first time, but I haven't really had a good argument from the code that you can't do it, except watch our for heat effect. I probably wouldn't ever do it on a large single family dwelling service, but industrial I would. Until tomorrow, thanks for all the help.