Need help ! I have a 12 story property fed by two switch gears. A 3000 amp main and a 1600 amp secondary. Built in 1984.
Backstory : we were hit hard by hurricane Helene storm surge . We had a phase to phase event in conduit between utility transformer and our gears. There are 13 parallel runs. 8 feed the 3000 and 5 feed the 1600. Two wires phased together in the 3000 side and 2 wires phased in the 1600 side. Salt water from conduits shot into each cabinet. The building was put on two generators to keep operation going.
Both breakers were removed and tested the 1600 was replaced after finding voltage leak by when open and a refurnished unit like for like was purchased . We finally had all 52 feeders cables replaced by insurance 6000ft of wire. Long story short we re energized with utility just this passed weekend after 7 months on generator power.
All is well with the 3000 side. This feeds my buss riser to the building, all floors and main elevators, and a 480 volt 400 amp disconnect for chiller 1.
1600 feeds my ATS , high voltage 277 garage lighting distribution and garage elevators panels, 400 amp disconnect for chiller 2 and a 480 / 277 volt sub panel for chiller plant pump motors and cooling tower drives.
The 1600 keeps tripping. What I thought originally was garage ground floor lighting submerged by storm surge causing issues . I have completely isolated the fused disconnect for that (HG 1/HG2 panels) by turning it off The 1600 switch remained stable for hours until I fired up chiller 2. Upon loading up. The breaker tripped again…. I’m at a loss. Are the ground fault settings too sensitive ? Is the shunt trip activating by itself ?
I am not an electrician, I operate the site as the building engineer. Any help or ideas would be great !
-M
Backstory : we were hit hard by hurricane Helene storm surge . We had a phase to phase event in conduit between utility transformer and our gears. There are 13 parallel runs. 8 feed the 3000 and 5 feed the 1600. Two wires phased together in the 3000 side and 2 wires phased in the 1600 side. Salt water from conduits shot into each cabinet. The building was put on two generators to keep operation going.
Both breakers were removed and tested the 1600 was replaced after finding voltage leak by when open and a refurnished unit like for like was purchased . We finally had all 52 feeders cables replaced by insurance 6000ft of wire. Long story short we re energized with utility just this passed weekend after 7 months on generator power.
All is well with the 3000 side. This feeds my buss riser to the building, all floors and main elevators, and a 480 volt 400 amp disconnect for chiller 1.
1600 feeds my ATS , high voltage 277 garage lighting distribution and garage elevators panels, 400 amp disconnect for chiller 2 and a 480 / 277 volt sub panel for chiller plant pump motors and cooling tower drives.
The 1600 keeps tripping. What I thought originally was garage ground floor lighting submerged by storm surge causing issues . I have completely isolated the fused disconnect for that (HG 1/HG2 panels) by turning it off The 1600 switch remained stable for hours until I fired up chiller 2. Upon loading up. The breaker tripped again…. I’m at a loss. Are the ground fault settings too sensitive ? Is the shunt trip activating by itself ?
I am not an electrician, I operate the site as the building engineer. Any help or ideas would be great !