hillbilly1
Senior Member
- Location
- North Georgia mountains
- Occupation
- Owner/electrical contractor
I think somewhere back in the beginning of this thread, the OP said it was feed from a sub breaker from the 1600 amp main?It might be time to hire a good industrial electrician or an engineer to come by and evaluate some of what you have going on. I can't tell if there are glaring issues or if I am only getting / understanding things partially. A 1600A breaker wouldn't be protecting a 275kW generator under normal circumstances. Potentially if it was only a back up for the fire pump. I wouldn't suggest replacing that breaker without consulting an engineer or experienced electrician any way since it is for the fire pump and emergency systems. There needs to be some coordination with the fire pump.