Can shunt trip breakers be used as a load management system to comply with 702.5(2)(b)?
It's an existing building that has a load of 30a more than what the fla of the generator is after the 125% multiplier. So, they are simply replacing a couple of the A/C breakers with shunt trip ones. Seems like a satisfactory soultion.I have noticed Target doing this on their old stores, they use a relatively small generator, I do not know if they do it on the new stores, strange but effective way of reducing load............
It's an existing building that has a load of 30a more than what the fla of the generator is after the 125% multiplier. So, they are simply replacing a couple of the A/C breakers with shunt trip ones. Seems like a satisfactory soultion.
Yep. Just interrupt the 24v control transformer's R (red) wire.Why not just interlock the A/C control voltage with relays? Much cheaper and does not have to be reset after a power outage.
Why not just interlock the A/C control voltage with relays? Much cheaper and does not have to be reset after a power outage.
After further consideration, that is what will be done. Thanks for the replysWhy not just interlock the A/C control voltage with relays? Much cheaper and does not have to be reset after a power outage.