Question that I was asked to ask here by my boss. He want to know if anyone knows how many amps can a 18/2 hold at 12 volts max?
5.6 amps
240.4 D(1)
Depends on how long you want it to hold that current. I would bet that it could sustain at least 20 amps for several hours, if not days, if not even indefinitely, without melting the insulation. Or were you asking about code restrictions? :wink:He want to know if anyone knows how many amps can a 18/2 hold at 12 volts max?
Actually it is 7 amps max OCP unless it is a continuous load then it would be 5.6amps OCP and the other conditions apply.5.6 amps
240.4 D(1)
I bet that 20a would melt the insulation.I would bet that it could sustain at least 20 amps for several hours, if not days, if not even indefinitely, without melting the insulation.
I bet that 20a would melt the insulation.
What would you like to bet?
I'm not so sure about that. My calculations show that a #18 copper with 20 amps of current flowing will reach the commonly accepted maximum short time temperature of 150?C in ~18.5 seconds. This is based on the formula that says a copper conductor will reach 150?C when you apply 1 amp for each 42.25 circular mils of the conductor area for 5 seconds. This value is 38.34 amps for the #18 (1620/42.25). You use this value to obtain the ampere squared second rating used to calculate the time to reach 150?C for other current levels. The ampere squared second value would be 38.34 * 38.34 * 5 = 7248.78. If we divide this value by 400 (20 amps squared) we get a time of 18.37 seconds for 20 amps to bring the #18 to 150?C.Name the bet.
I guarantee I can load it to 20 amps for many hours without damaging the insulation.
Roger
Sounds like a simple experiment is in order?
In free air?
Gar?
The bet's off then! Bah! Water cooled! Harumph! As if!Name the bet.
I would be force cooling it as in submerged in flowing cold water.:wink: