Ran into a very interesting trouble call today: 40 year old induction furnace system.
It appears to be converting 3 phase 60Hz into single phase 180Hz using nothing more than a transformer. I did not know this was possible, and was hoping someone could shed some light:
The transformer primary is a normal 480V delta. But the secondary has all three windings in series, additive polarity.
The beginning and the end of the series secondary are the single-phase feeders directly to the furnace.
My assumption is that each cycle on the 3 phase side is being used to generate a cycle on the common secondary, so multiply 60Hz x 3 = 180Hz. Is it really that simple?
Also, on the primary side there is what appears to be s big tuned LC circuit of inductors and capacitors in series, wired in parallel with the primary. Any idea the function?
Thanks.