bill@usps06492
Member
- Location
- Connecticut
I've been asked if it is okay to wire a line volage(120vac) t-stat with 18awg t-stat wire. The the wire terminates, with other control wires in the same j-box that provides the main power to the furnance, which is also 120vac. The concern is that the insulation on the t-stat wire is not rated high enough to be in the same box as the 12awg that provides the power to the furance. Art310.5 table it shows that the minimum size wire between 0-2000v to be 14awg. So to me it appears that even if the 18awg had the same insulation and could carry the current, the minimum the wire can be is 14awg.....
Has anybody come across a situation like before?
Bill
Has anybody come across a situation like before?
Bill