2nd time I have run into this method and really don't care for it. Inspector wants a 194 heat detector in the attic and firex doesn't make a 194 so the direction I have received is as follows: purchase an Edwards 282B-PL (rate of rise) which I know will give trouble signals. Should be fixed (Edwards 284B-PL)but that not important right now. He wants me to take a Firex Module # 0498 and a SP switch which is used to short the signal circuit of Firex smokes so a single person can walk around and check that each detector is connected. Instead of the switch I should wire a Edwards heat detector so when it goes off it signals all the firex to sound off. Note there is no DC backup AND if this unit were to burn out (never make contact at 194) no one would ever know it! Who's liable? Me of course it's my masters license. When this is complete I will send a registered letter to the state and notify them.
We use to put smokes in the attic and NEVER had an issue with them. I'll take smoke over heat in an attic anyday especially when there is equipment up there such as ac unit
Anyone else seen this disaster?
We use to put smokes in the attic and NEVER had an issue with them. I'll take smoke over heat in an attic anyday especially when there is equipment up there such as ac unit
Anyone else seen this disaster?