hardworkingstiff
Senior Member
- Location
- Wilmington, NC
1. To avoid long runs of cables (on floating piers) which contain a multiplicity of conductors, it is recommended that such cables be considered as feeders and branch circuits be taken off at junction boxes to provide service to shore power receptacle outlets and to float or pier lighting fixtures and equipped with overcurrent protection at the location of the equipment served by the branch circuit.
2. A cast metal junction box with a cast metal gasketed cover and containing the required number of properly sized and arranged terminals shall be installed on each individual floating section. the point of entrance of the cable into each junction box shall be protected by a marine type gland or terminal tube, threaded into the wall of the junction box and packed to prevent entrance of water or moisture into the box. The conductors shall be fitted with proper terminal lugs and equipment ground conductor shall be attached by a suitable screw or bolt to the interior of each junction box.
This is the 1st time the "junction box" required by 555.13(B)(4)(b) was introduced by the NFPA. I believe the receptacles used back then were of the 20-amp variety, not the 50 and 100-amp being used today. The intent of the "junction box" back then seems to be a place to take a large feeder and disperse to smaller loads. With current loads requiring a separate feeder to each power center, the "junction box" seems to have lost its purpose.
Am I wishful thinking, or do you think my perspective has merit?
2. A cast metal junction box with a cast metal gasketed cover and containing the required number of properly sized and arranged terminals shall be installed on each individual floating section. the point of entrance of the cable into each junction box shall be protected by a marine type gland or terminal tube, threaded into the wall of the junction box and packed to prevent entrance of water or moisture into the box. The conductors shall be fitted with proper terminal lugs and equipment ground conductor shall be attached by a suitable screw or bolt to the interior of each junction box.
This is the 1st time the "junction box" required by 555.13(B)(4)(b) was introduced by the NFPA. I believe the receptacles used back then were of the 20-amp variety, not the 50 and 100-amp being used today. The intent of the "junction box" back then seems to be a place to take a large feeder and disperse to smaller loads. With current loads requiring a separate feeder to each power center, the "junction box" seems to have lost its purpose.
Am I wishful thinking, or do you think my perspective has merit?