Michael Park
Member
I am involved in a project where we have installed recessed accent lighting in drywall ceiling bulkheads. The fixtures are tied together with EMT conduit and FMC, and contain only conductors of the multiwire branch circuits dedicated for lighting. Upon inspection of the installation, the code official for the AHJ stated that the fixtures must be listed as a raceway in order for the installation to be approved. I responded to this that according to the 1996 NEC, to which the project is contractually bound, Artcle 410-31, exception 2, dictates that the listing is not necessary. The code official then issued a statement stating that the exception 2 only applied to contiuously joined fixtures, and that the 2002 NEC clarified this by removing the exceptions to 410-31 and added 410-32. I have responded that the statement is false since Article 410-32 of the 2002 NEC still recognizes fixtures connected together with approved wiring methods do not require listings as a raceway. Could you please give me you opinion on this matter at your convenience?
Thank You.
Thank You.