For motor less than 1HP, 120VAC, let's say something like 3/4HP, 7.5A FLA.

- The SC/GF protection can be from 20A CB that feeds general use receptacle that will be source of supply
- The OL protection can be from the same 20A CB (motor is not automatically started, not permanent, is stationary, and will be within sight of controller)
- The Controller can be a switch as defined in 430.83(C)

So far so good. I just need some type of applicable switch, like a 15A snap switch, to be considered my controller.

But then the disconnect requirements...

- 430.102(A) Requires the controller to have a disconnect
- 430.109(C) States that the same type of switch that I can use as my controller, can be used as my disconnect

So can the same snap-switch be considered both the controller and the controller disconnect?

430.111 lists requirements for being both controller and disconnect. Would a snap switch be considered an air-break switch in this context? If not, it would almost seem like I would need a snap-switch upstream from my snap-switch.. which doesn't seem right. Hence my posting here.


Receptacle, switch, and motor all to be in same room.
 

bwat

EE
Location
NC
Occupation
EE
Need the switch be HP-rated?
I don't think so per 430.83(C) and 430.109(C)

Edit: A nice person would have posted the sections rather than just list them. Sorry.

430.83(C) Stationary Motors of 2 Horsepower or Less. For stationary
motors rated at 2 hp or less and 300 volts or less, the
controller shall be permitted to be either of the following:
(1) A general-use switch having an ampere rating not less
than twice the full-load current rating of the motor
(2) On ac circuits, a general-use snap switch suitable only for
use on ac (not general-use ac–dc snap switches) where
the motor full-load current rating is not more than
80 percent of the ampere rating of the switch

and
430.109(C) Stationary Motors of 2 Horsepower or Less. For stationary
motors rated at 2 hp or less and 300 volts or less, the disconnecting
means shall be permitted to be one of the devices
specified in (1), (2), or (3):
(1) A general-use switch having an ampere rating not less
than twice the full-load current rating of the motor
(2) On ac circuits, a general-use snap switch suitable only for
use on ac (not general-use ac–dc snap switches) where
the motor full-load current rating is not more than
80 percent of the ampere rating of the switch
(3) A listed manual motor controller having a horsepower
rating not less than the rating of the motor and marked
“Suitable as Motor Disconnect”
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Sounds like a single switch is okay, but I'd probably opt for one rated for greater current, like a 20a or 30a switch.
 