For motor less than 1HP, 120VAC, let's say something like 3/4HP, 7.5A FLA.
- The SC/GF protection can be from 20A CB that feeds general use receptacle that will be source of supply
- The OL protection can be from the same 20A CB (motor is not automatically started, not permanent, is stationary, and will be within sight of controller)
- The Controller can be a switch as defined in 430.83(C)
So far so good. I just need some type of applicable switch, like a 15A snap switch, to be considered my controller.
But then the disconnect requirements...
- 430.102(A) Requires the controller to have a disconnect
- 430.109(C) States that the same type of switch that I can use as my controller, can be used as my disconnect
So can the same snap-switch be considered both the controller and the controller disconnect?
430.111 lists requirements for being both controller and disconnect. Would a snap switch be considered an air-break switch in this context? If not, it would almost seem like I would need a snap-switch upstream from my snap-switch.. which doesn't seem right. Hence my posting here.
Receptacle, switch, and motor all to be in same room.
- The SC/GF protection can be from 20A CB that feeds general use receptacle that will be source of supply
- The OL protection can be from the same 20A CB (motor is not automatically started, not permanent, is stationary, and will be within sight of controller)
- The Controller can be a switch as defined in 430.83(C)
So far so good. I just need some type of applicable switch, like a 15A snap switch, to be considered my controller.
But then the disconnect requirements...
- 430.102(A) Requires the controller to have a disconnect
- 430.109(C) States that the same type of switch that I can use as my controller, can be used as my disconnect
So can the same snap-switch be considered both the controller and the controller disconnect?
430.111 lists requirements for being both controller and disconnect. Would a snap switch be considered an air-break switch in this context? If not, it would almost seem like I would need a snap-switch upstream from my snap-switch.. which doesn't seem right. Hence my posting here.
Receptacle, switch, and motor all to be in same room.