I'm looking to calculate the maximum amperage that I can ever read on the following two transformer scenarios.
Scenario 1:
Single phase 25kVA transformer 13.2kV x 120/240V. I calculated 25000VA/240V = 104A as the maximum current reading that I'll measure across the secondary bushings hot leg to hot leg. Is that correct?
Scenario 2:
(3) single phase 25kVA transformers banked together (or one 3 phase 75kVA transformer). 13.2kVA x 120/208V. Here is where I'm confusing myself. When trying to calculate the max. amperage that I can get out of this bank, what values are used? Do I use 75000VA/208V = 360A total or 120A per transformer? In this scenario the secondary windings are paralleled, so I'm getting 120V L-G out of each transformer.
Thanks
Scenario 1:
Single phase 25kVA transformer 13.2kV x 120/240V. I calculated 25000VA/240V = 104A as the maximum current reading that I'll measure across the secondary bushings hot leg to hot leg. Is that correct?
Scenario 2:
(3) single phase 25kVA transformers banked together (or one 3 phase 75kVA transformer). 13.2kVA x 120/208V. Here is where I'm confusing myself. When trying to calculate the max. amperage that I can get out of this bank, what values are used? Do I use 75000VA/208V = 360A total or 120A per transformer? In this scenario the secondary windings are paralleled, so I'm getting 120V L-G out of each transformer.