1PH/3PH RECEPTACLE

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Ok, yes prob dumb question. So there is a 2 pole breaker feeding these receptacles. The receptacle type can either be a 1 phase or 3 phase. It would have to be a single phase receptacle I'm assuming. But how could a single phase receptacle be matched with a 2 pole breaker? Thanks.
 

Attachments

  • Capture.jpg
    Capture.jpg
    30.1 KB · Views: 0

kwired

Electron manager
Location
NE Nebraska
You only have one phase angle between two "phase conductors" so the connected load is "single phase". "Single phase" does not have to be "line to neutral".
 

meternerd

Senior Member
Location
Athol, ID
Occupation
retired water & electric utility electrician, meter/relay tech
Thank you!

This may be a terminology problem. Single phase seems to refer to one line (hot) and one neutral. But...when a receptacle is set up for two hot lines, one neutral and one ground it's still often referred to as single phase. The voltage between the two hots may be 208, 240 or 480 depending on the transformer supply.
 