There is a distribution transformer 45kVA, 3ph, 4w, 480-208Y/120V, feeding three separate disconnect switches (fused) 100AS 70AF. (Assumption:
disc SW 1: AB;
disc SW 2: BC;
disc SW: AC)
One of this disconnect switches is a spare and they want to feed an old office trailer with it. The trailer needs a brand new panelboard (loads on that trailer: A/C unit + lighting). I was going to order a 1 phase, 240/120V, 100A main, (1) 2-pole 60A CB and (10) 1-pole 20A CB. However, I just want to make sure I’m doing things right:
- Is my assumption that each disconnect switch is AB, BC and AC?
- Can I have a 1ph 240/120V panel even though the upstream transformer is a 3ph 208Y/120V? This question comes because I can’t understand how to go from a 208V (line-to-line), 3 ph panel to a 240V (line-to-line), 1 ph panel.
I would understand that with a single phase transformer you can get 120V or 240V on the secondary depending how you wire the terminals X1, X2, X3, X4, but I can’t get my head around how you get 240V when the transformer is a 3ph 208Y/120V. what am I missing?
The HVAC unit is 240V so i would need that voltage after all.
thank you!
disc SW 1: AB;
disc SW 2: BC;
disc SW: AC)
One of this disconnect switches is a spare and they want to feed an old office trailer with it. The trailer needs a brand new panelboard (loads on that trailer: A/C unit + lighting). I was going to order a 1 phase, 240/120V, 100A main, (1) 2-pole 60A CB and (10) 1-pole 20A CB. However, I just want to make sure I’m doing things right:
- Is my assumption that each disconnect switch is AB, BC and AC?
- Can I have a 1ph 240/120V panel even though the upstream transformer is a 3ph 208Y/120V? This question comes because I can’t understand how to go from a 208V (line-to-line), 3 ph panel to a 240V (line-to-line), 1 ph panel.
I would understand that with a single phase transformer you can get 120V or 240V on the secondary depending how you wire the terminals X1, X2, X3, X4, but I can’t get my head around how you get 240V when the transformer is a 3ph 208Y/120V. what am I missing?
The HVAC unit is 240V so i would need that voltage after all.