Certainly OK to do that. You simply abandon the poles you don't need. Or repurpose them for another circuit, if you'd like to switch multiple circuits at the same time.Anyone ever install a 3phase disconnect and use it as a single phase disconnect. Basically use the 3phsse as 1phase
It's common that unfused units may only be available in 3-pole options, while the fused counterparts are built for both 2-pole and 3-pole options.
I'd expect that the HP rating of a disconnect would correspond to the same Amps per pole at the same voltage. This means I'd expect the single phase HP rating to be 57.7% the 3-phase HP rating. I.e. 1/sqrt(3).That 3 phase unit may have a different HP rating and may not be suitable for 1 phase. It will say on the label
Service equipment requires that you have a fused disconnect anyway, so you aren't put in a situation where the only viable product would require the abandoned pole. You can get disconnects that are purpose-built to the required number of poles, and usually the 2-pole unit is slightly cheaper than the equivalent 3-pole unit. It still has mostly the same components, just with a blade and a fuse holder omitted from the assembly.What about as service equipment? If so what would be a good argument to make to inspector
The horsepower rating is applicable for the making and breaking of a single motor locked rotor/starting current. If there are multiple motors fed by this switch its HP rating is immaterial.I'd expect that the HP rating of a disconnect would correspond to the same Amps per pole at the same voltage...
Listed multi-pole overcurrent protective devices have been tested to protect all of the various pole configurations possible; a 3-pole device has been tested with 1, 2, and 3 pole configurations.I'm not aware of any code rule that either permits or prohibits abandoned poles on service disconnects.