Danpc1979
Member
- Location
- Cranston RI
on a job in a very nice place and I came across some bonding issues.
I have a generator that I confirmed that is bonded,it has a main breaker to disconnect the MDP from it, confirmed neutral to ground and enclosure bond at generator. Then I confirmed MDP isolated neutral and SDP isolated neutral. Concerning branch circuit every one has an isolated neutral. What I learned from all of article 250 an 240 in NEC this would be an exceptable installation. Can you fellow electricians that are more advanced than me in the trade confirm this also. Thanks, Dan.
I have a generator that I confirmed that is bonded,it has a main breaker to disconnect the MDP from it, confirmed neutral to ground and enclosure bond at generator. Then I confirmed MDP isolated neutral and SDP isolated neutral. Concerning branch circuit every one has an isolated neutral. What I learned from all of article 250 an 240 in NEC this would be an exceptable installation. Can you fellow electricians that are more advanced than me in the trade confirm this also. Thanks, Dan.