ptonsparky
Tom
- Occupation
- EC - retired
Small industrial customer called with VFD that would not stay online. One of the 5 motors it controls had failed. During the "tell me" stage of the service call the customer noted that a couple months ago they had changed out 2 of the 5. The load side of the drive feeds a terminal block that has 5 manual motor starters tapped from it to each of the 5 motors. The two motors they installed ran backwards so they switched 2 of the leads from the drive to the terminal block, pretty obvious by the way the wires lay. Afterwards all 5 ran the correct direction. Is this possible or am I not quite hearing the whole story? Happens, very rarely and only to me I am sure.