Utility's strenght member is in the grounded conductor,,,cut it with your strippers it will nick the blades.
i'm still trying to come up with a correction notice for this unpermitted barn that has recently been annexed into our city.
in addition to other violations, this is the last thing. they ran (overhead) to the 100A sub. at least they used insulated supports on the poles! i know it is not a "service" conductor, but is there any code that allows (or disallows) this?
really 0'0" ????...the service utility does it all the time without a "messenger" wire
then what's this about?
.......really 0'0" ???? the service utility does it all the time without a "messenger" wire...
I would say 0'-0". It's not rated for installation like that.
If, however, you install a messenger............
btw- how much do you want to lose?
do i need to post the definition of "messenger wire" ?
i have the 05 nec , where is ACSR allowed? hmmmm.
well, i can show you where i can span 15' (per CODE) without a messenger wire, and also when one is required (per CODE)..
do you need to knwo where to send the $$$$???
If it is the utility: a lot longer than you would ever be worried about. The sag will manage the tension. We will pull 2/0 hard-drawn copper in at a maximum design tension of 2,963 lbs. For a 2,000 span, that is a 69 ft sag. For a 200 ft span, that is a 0.7 ft sag.what is the max unsupported span (no guy wire) for 2/0 copper??
argggg, i can't find anything!!!!
Not necessarily.Utility's strenght member is in the grounded conductor,,,cut it with your strippers it will nick the blades.
Has nothing to do with copper service.Wanna bet? What do you think ACSR stands for?
The grounded conductor is not necessarily the support.thnaks.. i found the 225.6 reference. for some reason, i thought there was a table indicating max span based on conductor size:-?
nice tip on the grounded conductor being used by the utility , i wondered how they did that. i don't deal with their side of the panel...
thanks!