Is there some Code section that allows the use of a #12 AWG (copper) EGC with #10 AWG line and neutral conductors? According to one of the older guys I work with it used to be allowed (he still marks plans that way out of habit, and then has to go back and correct himself), although I'm not sure how long ago that was. The oldest NEC book I have available is 1993, and it seems to have pretty much the same requirements as the 2008, which is the code cycle I'm working under right now (although in 1993 it was Section 250-95). The only real difference I see is that the 1993 NEC only required increasing the size of the EGC when the ungrounded conductors were increased due to voltage drop, whereas beginning in 2002 NEC doesn't care why the ungrounded conductors were increased in size.
As I understand it, Table 250.122 requires a #10 copper EGC for a 25 or 30 amp circuit (i.e. a circuit that would require #10 copper line and neutral conductors without any derating). For a 20 amp circuit with #10 copper line and neutral conductors, the EGC would also have to be increased to #10 per NEC 250.122(B). These requirements haven't changed since 2002.
However, lately I've seen several sets of approved plans calling for circuits with 2#10 and 1#12 EGC. If memory serves, all of these circuits have been 120 volts, 20 amps, feeding general use receptacles. These plans are all pretty recent (between 2005 and 2012), and I'm starting to wonder if there's something I've missed in my reading of the Code regarding this issue.
So... do you know of anything in the NEC that would permit running a #12 EGC with #10 line and neutral?
As I understand it, Table 250.122 requires a #10 copper EGC for a 25 or 30 amp circuit (i.e. a circuit that would require #10 copper line and neutral conductors without any derating). For a 20 amp circuit with #10 copper line and neutral conductors, the EGC would also have to be increased to #10 per NEC 250.122(B). These requirements haven't changed since 2002.
However, lately I've seen several sets of approved plans calling for circuits with 2#10 and 1#12 EGC. If memory serves, all of these circuits have been 120 volts, 20 amps, feeding general use receptacles. These plans are all pretty recent (between 2005 and 2012), and I'm starting to wonder if there's something I've missed in my reading of the Code regarding this issue.
So... do you know of anything in the NEC that would permit running a #12 EGC with #10 line and neutral?