can one have two 120V feeding two recept. in the same two gang box. I know 404.8 talks about snap switch and other devices being adjacent and 300V limit.
thank in advance
Ace :confused:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 2/120v in same box

Absolutly, this can even be on one duplex receptacle if you follow the requirements of 210.4(B) or 210.7(C)

Roger
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: 2/120v in same box

With two 120 devices, would the maximum voltage be more than 300V if they were on L1 and L2?
 
Re: 2/120v in same box

i appreciate the answer Roger.
Mr baker, I don't think it can be more than 240V. 2x120 if on L1 and L2 and 0 if both on L1 or L2. it's a typical residential wiring. my problem with the wording of 404.8 is that it state SNAP SWITCHES adjacent to other devices..
Thanks again
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: 2/120v in same box

Ace-where this rule applies is for 277V lighting circuits. A slight wording change for the 02 NEC clarified it could be any two adjacent devices, not just snap switches.
 