N ndc81167 Member Aug 12, 2018 #1 i have a 100amp single phase main breakers feeding 1- 20 circuit panel ,, and from that panel i have a 90mp breaker feeding another 100amp 20 circuit panel . is this code complaint ? i cant find anything prohibits this .
i have a 100amp single phase main breakers feeding 1- 20 circuit panel ,, and from that panel i have a 90mp breaker feeding another 100amp 20 circuit panel . is this code complaint ? i cant find anything prohibits this .
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Aug 12, 2018 #2 Yes code complaint.
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Aug 12, 2018 #3 I agree with Infinity. 100A main, 90A sub......SER to sub?
kwired Electron manager Location NE Nebraska Occupation EC Aug 12, 2018 #4 Second panel is now effectively a 90 amp panel, even if it had a 200 amp main breaker in it.