I have a run of 2.5" schedule 80 pvc where I need to utilize a pvc l.b.
I found a 2.5" lb that is rated for 3 350 mcm wire fill..
The largest wire that my run will use is 2 - 250 mcm wires plus some smaller wires.
The combination of all my wires at 40 % fill is 1.530 inches.
The fill of 3 350 mcm wires is 1.5498 inches.
Will this work ?
note....wires have already been upsized to allow for 80% fill...
Thanx...dhsvcs