2.5 Volts on Outdoor Shower

Jimmy7

Senior Member
Location
Boston, MA
Occupation
Electrician
First and foremost, I hope everyone has a Happy July 4th. In 2022, I upgraded my mother-in-law’s service in her single family home on Cape Cod to 200 amps. The soil here is a mix of sand because it’s a mile or so from the beach. In any case, we’re here on vacation this week and last night my son went to use the outdoor shower where he said he felt some tingling. This morning I put my meter on it and sure enough I got 2.5 volts ( From the faucet to the soil). When I did the service I drove two ground rods outside and then bonded the copper pipes inside, the water pipe coming in from the street is plastic. Is this voltage caused by a problem with the neutral? Could this be at the utility pole?
 

MD Automation

Senior Member
Location
Maryland
Occupation
Engineer
It’s possibly a utility problem.

If you are onsite, the first thing to do is see if the problem exists at the main – as compared to an issue w/ some branch circuit wiring.

Easiest test is to shut off everything at the main panel and measure both L-N voltages and L-L. You should see 120-120-240 (I'm assuming a typical single phase service), or something close to that, but hopefully pretty balanced between legs.

Then load up one side of the service with a decent current draw – toaster, hair dryer, shop vac. Needs to be a single phase 120 load. Then repeat those measurements above.

You are looking to see if you can get the Neutral to swing towards one leg. So the balance might then be something like 117-123-240. If that happens, you know there is a weak neutral upstream. Either right there in connection to the neutral bar, in the meter can, or the lateral out to the transformer.

If this test shows good balance between legs, then the problem is likely downstream in some branch circuit wiring.

If you do get the POCO onsite – a classic failure on their part is to pull the meter and measure voltages. And they declare all is good on their side and leave. Naturally, with no current flowing, the weak neutral problem is not "exposed". Either show them your test, or ask them to load the service themselves. A good lineman will have a “Beast of Burden” tester on the truck and know how to use it.

Good luck.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
When I did the service
I grew up in a college town, where neighbors rented out backyard auxiliary dwelling unit (ADU) hack jobs with outdoor showers for the college kids.

The makeshift ADU's are typically not sophisticated, so the showers come from an exterior hose bib, and outdoor & exposed Romex feeders get trampled underfoot with egress.

Looks like Cape Cod has several towns with colleges and universities.
 

Jimmy7

Senior Member
Location
Boston, MA
Occupation
Electrician
I have some more information. There is a utility pole behind house for the street behind the house (Not the pole that feeds the house). The pole has an abandoned temp service still hooked up plus a transformer at the top of the pole. I ran a wire from my house ground and the closer I got to this pole the higher the voltage got.
 
Last edited:

Eddie702

Licensed Electrician
Location
Western Massachusetts
Occupation
Electrician
I have some more information. There is a utility pole behind house for the street behind the house (Not the pole that feeds the house). The pole has an abandoned temp service still hooked up plus a transformer at the top of the pole. I ran a wire from my house ground and the closer I got to this pole the higher the voltage got.
That's good troubleshooting. I would put an Amprobe on the GEC and see if you're reading anything. If you read something and it goes away when you kill the main the problem is in the house. If you have current on the GEC and it stays when you kill the main the problem is an outside source
 

MD Automation

Senior Member
Location
Maryland
Occupation
Engineer
Just to clarify a point I did not fully explain in my post#2...

What you are really looking for in my test is an increase in the L-N voltage of the leg you did NOT put the load on. There are various reasons why you might see a voltage drop in a circuit - but to see the voltage go up (with the L-L reading staying basically the same) ... that's a huge clue pointing to a weak neutral.
 