2 adjacent things with earthing requirements

Status
Not open for further replies.
Say I have an outdoor pad Mount utility transformer and a service disconnect in close proximity to each other, let's say 8 to 10 ft. Let's say the utilities spec is typical where the secondary center tap is bonded to the transformer case and connected to a grounding electrode. If the distribution system is a MGN we will also have the primary neutral connected to the xformer can, but whether it's an MGN or a Delta shouldn't effect the answer to this question. The question is do I use the same grounding electrodes for both the utility grounding and for the service disconnect grounding, or keep them separate? Would the answer be the same if the transformer was a customer owned SDS?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I think I always think you can use the same electrodes if you want. Earth is earth. Unless someone involved (utility?) has some dumb rule to the contrary.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Generally, electrode systems can be shared, but this will create a parallel neutral-current pathway.

Transformers and disconnects aren't usually so close, and earth is not considered a current path.
 

BackCountry

Electrician
Location
Southern California
Occupation
Licensed Electrician and General Contractor
Say I have an outdoor pad Mount utility transformer and a service disconnect in close proximity to each other, let's say 8 to 10 ft. Let's say the utilities spec is typical where the secondary center tap is bonded to the transformer case and connected to a grounding electrode. If the distribution system is a MGN we will also have the primary neutral connected to the xformer can, but whether it's an MGN or a Delta shouldn't effect the answer to this question. The question is do I use the same grounding electrodes for both the utility grounding and for the service disconnect grounding, or keep them separate? Would the answer be the same if the transformer was a customer owned SDS?

Where I’m at, their electrode is inside the pad next to their ducts, so we’d never be able to get access to it, and the GEC would have to be inspectable at the service entrance? If their rod is not inside the pad footprint, then I think the only thing holding you back is the utility rules.

If it was a customer owned transformer, then you’re for sure in the clear — as long as it’s inspectable.

I have, and regularly do, share the same rod with clustered equipment — even though I usually get a weird look, I’m not into driving rods in proximity because they want to see it that way or the plan shows it that way because distance wasn’t factored in.

Likewise, I absolutely refuse to sink a rod on ground mount PV projects with driven piles, helical piers, or screw piles. 100 bonded 7ft embedment C channels… and a ground rod. No way.
 
FWIW, let's say in the case of utility transformer I am installing the pad and ground ring with two rods for their specs so there is no issue with access, different timing etc.

On one hand, I don't like the parallel path created through the gec's. On the other hand, I like having everything bonded together, but of course the neutral conductor is bonding them together,. So I guess the gecs was shared electrodes just make it "more bonded together"🤔
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
How about a couple one lines to aid in responses.
I do have a few thoughts.
One is bonding versus grounding.
Service versus SDS
 