I have a question for someone with an answer. We've run into a bit of a problem. We ran alot of #2AL XHHW-2 to some storage units. Each unit has its own 100A service single phase. These are feeders coming out of a meter bank. Each feeder is piped individually with 2 hots, 1 neut, and 1 ground. They are direct buried for I would say 98% of their run. They then come above ground in pipe to an LB and into the building. We had each line protected with a two pole 100A Main breaker when leaving the meter bank.
Now, 310.16 shows #2AL XHHW-2 has a 90 deg rating and is rated at 100A, The 75 deg rating is 90A (thats 167deg F). The inspector says to go with the breaker rating of 75 deg(which is what I was thinking)
This is in Ohio, the temp goes from 0 deg F, to 100 deg F. Probably average would be around 60 deg F. I think there would be a correction factor that could be used to get this over 90A in the 75 deg column being the Ohio never sees 167 deg F. The inspector says in the sun it can go past that temp and overheat the breaker. But we're talking about the wire, not the breaker. Anyway, I would like to find a correction factor that would allow me to use 240.4B.
Pretty much the inspector wasn't convinced either way so he got another inspectors opinion, then they both weren't sure what to think about it so after about 30min of debate he wanted to error on the side of caution and recomend using a smaller size breaker.
The owner says no way, he wants 100A breakers. Any advice? Thanks
BTW, I do recall something about I think it was service wires being able to run something like 125% their rated ampacity. Is there something like that or was I dreaming that, and if there is such a code would it apply to feeders? Thanks again
Now, 310.16 shows #2AL XHHW-2 has a 90 deg rating and is rated at 100A, The 75 deg rating is 90A (thats 167deg F). The inspector says to go with the breaker rating of 75 deg(which is what I was thinking)
This is in Ohio, the temp goes from 0 deg F, to 100 deg F. Probably average would be around 60 deg F. I think there would be a correction factor that could be used to get this over 90A in the 75 deg column being the Ohio never sees 167 deg F. The inspector says in the sun it can go past that temp and overheat the breaker. But we're talking about the wire, not the breaker. Anyway, I would like to find a correction factor that would allow me to use 240.4B.
Pretty much the inspector wasn't convinced either way so he got another inspectors opinion, then they both weren't sure what to think about it so after about 30min of debate he wanted to error on the side of caution and recomend using a smaller size breaker.
The owner says no way, he wants 100A breakers. Any advice? Thanks
BTW, I do recall something about I think it was service wires being able to run something like 125% their rated ampacity. Is there something like that or was I dreaming that, and if there is such a code would it apply to feeders? Thanks again