Here is another ROP the issue is a bit different but they fully understand the exception and what it allows
4-43 Log #3384 NEC-P04
Final Action: Reject
(230.40 Exception No. 1)
______________________________________________________________
Submitter:
Frederic P. Hartwell, Hartwell Electrical Services, Inc.
Recommendation: Revise text to read:
If the number of service disconnect locations for any given classification of
service is not more than six, the requirements of 230.2(E) shall apply at each
location. If the number of service disconnect locations is more than six for any
given supply classification, all service disconnect locations for all supply
characteristics shall be clearly described using suitable graphics or text or both
on one or more plaque(s) located in an approved, readily accessible location(s)
on the building or structure served and as near as practicable to the point(s) of
attachment or entry(ies) for each service drop or lateral.
Substantiation:
Some control over the potential proliferation of service
disconnects at widely dispersed locations is needed by the inspection
community, preferably without resort to 90.4. In the comment period for the
2005 NEC the panel seemed to be moving in this direction, having accepted
part of this concept. However, that action was set aside by the TCC, giving
CMP 4 a fresh opportunity to consider these questions. This proposal responds
to concerns in the voting on 2005 NEC Proposal 4-71 that when the exception
is applied to allow a large number of remote service entrance conductor sets
and their disconnects, it may become unwieldy to provide full reciprocal
labeling at each location.
The proposal suggests a limit of six disconnecting means, considered for each
classification of supply characteristics. Suppose, for example, there were one
480Y/277V service for large power loads using a single disconnect at the
owner’s mechanical room and one 208Y/120V service with service entrance
conductors run to each of ten occupancies with service disconnects in each.
Assuming each occupancy does not qualify as a separate building, this wording
would result in either one or two plaques (instead of eleven) depending on
whether the two service drops or laterals arrive at the same or at different
locations. The proposed text includes the word “approved” in order to allow the
AHJ to review the proposed locations for suitability.
Panel Meeting Action: Reject
Panel Statement:
The permission to use 230.40, Exception No. 1 has been in
the NEC for the past 60 years in one form or another without a requirement for
location plaques to be installed at each disconnect location. Where there are
more than six disconnect locations, the proposal would require all supply
characteristics to be clearly described using graphics or text or both on a
plaque. Locating this graphic/text plaque on the building in a readily accessible
location that is acceptable to the authority having jurisdiction, usable for any
location identification, and that is as near as practicable to the point of
attachment or service entrance entry into the building would be extremely
difficult on all but the smallest buildings.
A large building or a high-rise building in a city is often on the exact
footprint of the city lot with underground service laterals supplying a utility
company vault. Even smaller buildings are often supplied with underground
service laterals so the entrance into the building is not obvious so a plaque
installed at the point of entrance of the service conductors into the building
would only be of use where someone searched for the plaque. In an emergency
situation, another power disconnection point would most often be used rather
than a search made for the plaque first and then an attempt made to disconnect
power at multiple locations.
The submitter has not provided any substantiation that there is a problem with
not marking these locations for the last 60 years. There does not seem to be a
large number of people submitting proposals to require these plaques for
installations where multiple occupancies exist with multiple disconnect
locations. The suggested recommendation has too many unenforceable
requirements.
Number Eligible to Vote: 10
Ballot Results:
Affirmative: 10
______________________________________________________________