jeff48356
Senior Member
- Location
- Livonia, Michigan
According to the ampacity table at 310.15, #2 AWG aluminum is good for 75 amps in the 60-degree column, since that's the one we're supposed use when dealing with cables rather than individual conductors. Since 75A is not a standard size, we're allowed to use the next higher breaker, which would be 80A. Is that the proper size breaker when using #2 SER AL to feed a subpanel? Or what would most people usually use?