2 breaker panels?
bootsan
Lakewood, WA
First I hope this is the right forum. I am a home inspector in Washington State and have just finished inspecting a home and found the following. The home used to be a duplex, it was renovated and made into a single family unit. There are still 2 breaker boxes with seperate meters. Is this an issue that I need to have a licensed electrician evaluate? My client was concerned about the 2 meters and receiving 2 bills each month. Code issue?
Thank-you
charlie
Indianapolis
Re: 2 breaker panels?
Unless they are located next to each other (grouped), they are in violation of the Code. It may not take that much to remove one of them and feed the other one from the first.
Bottom line, yes, he should be in contact with an electrical contractor since the use of the structure has changed. :D
petersonra
Northern illinois
engineer
Just curious why it would be a code violation to have 2 meters. I have heard of a fair number of people who have 2 meters.
don_resqcapt19
Illinois
retired electrician
Pete,
230.2 Number of Services.
A building or other structure served shall be supplied by only one service unless permitted in 230.2(A) through (D).
Don
charlie b
Seattle, WA
Electrical Engineer
It might not be a problem. When the building was a duplex, it is likely that the two meters each fed a separate panel, one panel for each of the two households. My question would be, what happened to the two panels during the renovation?
Do you still have two panels, each being fed from one of the two meters? If so, then (1) Yes, the customer would get two bills, and (2) It is a violation of 230.2.
But if one panel has been removed, so that all loads are powered by the other panel, OR if one of the panels has been configured to be sub-fed from the other, then 230.2 does not come into play. The building would only have one service, and it would have an unused extra meter on the wall. In this case, the homeowner should ask the utility to remove the unused meter.
bootsan
Lakewood, WA
Thank-you all for the replies. 2 seperate drops, into 2 seperate meters feeding 2 seperate panels. They are within 5 feet of each other, but not connected. I will be recommending a review by a licensed electrician.
Again as always thank-you for the replies.
jimwalker
TAMPA FLORIDA
is there by chance a 2 hour wire rated wall between them ? if so it might be actually 2 buildings.
I have done this on several townhouse and they are seperate buildings joined together
bootsan
Lakewood, WA
No seperation. I believe it used to be a large single family home then converted to an upstairs/downstairs duplex type home. Now someone has purchased it and converted it back to a single unit.
jimwalker
TAMPA FLORIDA
Having 2 meters might actually save them money as KW charges go up after so much usage.
I cant see any more danger than it had when it was 2 apartments
But i think it violates NEC
If it has 2 seperate risers then it is 2 services
If it has 1 riser maybe it could be argued that it is one service with 2 meters
charlie
Indianapolis
Jim, that would make the serving electric utility different from all the other electric utilities in the country! We have a customer charge which covers the meter reading and maintenance of the service for each meter. Additionally, we charge the highest rate for the first step in the rate. The more you use, the less you get charged for the energy usage.
If a customer adds an extra meter for service to his garage, he will pay approximately $100 per year for the extra meter if he doesn't even use any energy. Generally, the energy he uses will cost him at our highest rate since he would normally use so little in a garage. :D
jimwalker
TAMPA FLORIDA
My Progress Energy bill this month.
customer charge $8.03
first 1000 kwh---1,000 kwh @ 4.42700 cents = 44.27
above 1,000 kwh --1514 kwh @ 5.42700 cents =82.16
fuel charge 2,514 kwh @ 3.45800 cents =86.93
total electric cost 221.39
gross receipts tax 5.68
total current bill = 227.07
thats how it is here just north of Tampa FL
And i am not convinced that this install is illegal
[ October 20, 2004, 05:01 PM: Message edited by: jimwalker ]