2 Buildings - Electrical Service

Status
Not open for further replies.

Gshell82

Member
Location
Boston
If 2 separate buildings right next to each other are owned/maintained by the same owner, is it more common to provide 1 transformer & 1 service to both buildings (1 service to one bldg. then feed the other bldg.) or is it more common to have 2 transformers with separate service to each bldg?


Thanks
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
If 2 separate buildings right next to each other are owned/maintained by the same owner, is it more common to provide 1 transformer & 1 service to both buildings (1 service to one bldg. then feed the other bldg.) or is it more common to have 2 transformers with separate service to each bldg?


Thanks

I would think it is more common to have 1 transformer with a separate service to each building.
 

kwired

Electron manager
Location
NE Nebraska
I see it both ways quite often, or even both fed with service conductors from same source.

Some POCO may only want to supply one line to a customer premises though.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
If 2 separate buildings right next to each other are owned/maintained by the same owner, is it more common to provide 1 transformer & 1 service to both buildings (1 service to one bldg. then feed the other bldg.) or is it more common to have 2 transformers with separate service to each bldg?


Thanks

Is it the same property or two separate parcels?
 