I am working for a client who wants to add a generator to power two 30-ton trane chiller units. Each chiller has a Minimum Circuit Ampacity Rating of 146A and a Max Fuse size of 200A. I figured I could feed off of a 400A Breaker in the MDP with 400A rated conductors into a 400A exterior rated ATS then hitting a 400A exterior rated fused disconnect. From there have 200A rated feeders go into each of the Chillers. Oh yeah, and the chillers are at 1Kva per ton so i was figuring around a 75kva Generator.
146 + 146 = 292
292 * 1.25 = 365
400A Rating for the equpiment listed above. Do these numbers make sense?
146 + 146 = 292
292 * 1.25 = 365
400A Rating for the equpiment listed above. Do these numbers make sense?