Re: 2 Circuits, 1 Neutral, 2 Legs?
When the circuits are on opposite "phases," the neutral only carries the imbalance of current that is between the "hot" (ungrounded conductors). This priciple applies to any shared neutral circuit.
Say you have 10 amps on one circuit, and 5 amps on the other. The "neutral" will be carrying 5 amps.
Now, same circuit, but now both hots are carrying 10 amps, then these currents will cancel each other out and the neutral current will be 0 amps.
Take the same situation, but now consider the "hots" are on different breakers but the same phase. Each "phase" is carrying 10 amps. Now the neutral will carry 20 amps. If we are using #14 wire, the neutral will be overloaded.
It should be noted that almost every service in the United States is a multiwire cicuit of some type, either single phase or 3-phase. The service "neutral" carries the imbalance of current from the phase conductors.