infinity said:If there are two EGC's from two different cables with two different circuits are they required to be connected together? I say no. If each one goes directly to a device an interconnection is not required.
raider1 said:Agreed, but if they splice in the box then they must be connected together.
Chris
That's an oxymoron.infinity said:. . . the rest can simply be spliced straight through.
So I have a big vertical riser box filled with 500 Kcmil feeders w/ #4/0 EGC's, say 20 sets. I choose to splice all of the feeders at a midpoint in the run. Are you saying that I need to splice together all 20 #4/0 EGC's? I say that the only requirement is that the box is grounded to one of them and that the rest can simply be spliced straight through.
infinity said:If there are two EGC's from two different cables with two different circuits are they required to be connected together? I say no. If each one goes directly to a device an interconnection is not required.
iwire said:I disagree, 250.148 specifically mentions conductors terminated on equipment. Devices are equipment.
infinity said:I'm hung up on the fact that the requirement is for "any equipment associated with those circuit conductors". If EGC is for a 120 volt receptacle and the others are for a 277 volt circuit spliced within the box I don't see how the 277 volt EGC is "associated" with the 120 volt circuit conductors.