macmikeman
Senior Member
- Location
- Planet macmikeman
So this is what I have always considered "outside branch circuit and feeders, Article 225 of the NEC. In which case I put a 100 amp 2 pole service rated disconnecting means ( breaker enclosure with 2 pole 100 a breaker also) on the second building which I just wired. I did not bond between the grounded bus and the equipment grounding bus and inspector Is basically telling me I need to bond that once again at the outside disconnect on the building. I didn't want to get into a big argument with him although I did keep saying it is a 4 wire feeder, and the bond between neutral and ground happens in the first building. He says the 2nd building falls under 230 not 225. I disagree. Mind you 2nd building has 2 bedrooms, 2 baths, laundry, living room , kitchen , and lanai. I think he is wrong . I think I just need a "service rated " disconnecting means on the exterior side of the smaller house, and a single ground rod and #6 bare copper run to it from the above mentioned disconnecting means, and no neutral to ground bonding anywhere in that smaller house, interior 100 amp lugs only panel included. Also I am under the impression I don't have to create a water pipe gec for this 2nd house , although I made a bond to the water piping system from my panel to the pipes nearby at the water heater using bare #6 cu. Who's right, Me or Him?