B brian ploskunak Member May 31, 2006 #1 I am installing a 120/208 volt panel and a 277/480 volt panel at a separate building. Both feeds come from the same main building. Do I ground both panels to (1) grounding electrode system at the separate building?
I am installing a 120/208 volt panel and a 277/480 volt panel at a separate building. Both feeds come from the same main building. Do I ground both panels to (1) grounding electrode system at the separate building?
George Stolz Moderator Staff member Location Windsor, CO NEC: 2017 Occupation Service Manager May 31, 2006 #2 Yes, see 250.32(A), 250.50, 250.58.
B brian ploskunak Member May 31, 2006 #3 Yep, 250.58 says it right there in black and white! Thank you George.
George Stolz Moderator Staff member Location Windsor, CO NEC: 2017 Occupation Service Manager May 31, 2006 #4 De nada.