If I have a 400 amp meter/main on a pole with 2 runs (feeders) to a dwelling then I am in violation however, if I have a meter with no ocpd's at the pole then I can run 2 sets of service conductors from the meter to 2 separate 200 amp panels at the dwelling. I believe this to be true....
My question is why? Is one more dangerous than the other?
I was looking at 230.2 and 230.40 exception 2 to verify that 2 sets of service conductors would be considered one service. Am I reading this correctly?
My question is why? Is one more dangerous than the other?
I was looking at 230.2 and 230.40 exception 2 to verify that 2 sets of service conductors would be considered one service. Am I reading this correctly?
230.2 Number of Services. A building or other structure
served shall be supplied by only one service unless permitted in
230.2(A) through (D). For the purpose of 230.40, Exception
No. 2 only, underground sets of conductors, 1/0 AWG and
larger, running to the same location and connected together at
their supply end but not connected together at their load end
shall be considered to be supplying one service.
230.40 Number of Service-Entrance Conductor Sets. Each
service drop, set of overhead service conductors, set of underground
service conductors, or service lateral shall supply only
one set of service-entrance conductors.
Exception No. 2: Where two to six service disconnecting means in separate
enclosures are grouped at one location and supply separate loads
from one service drop, set of overhead service conductors, set of underground
service conductors, or service lateral, one set of service-entrance
conductors shall be permitted to supply each or several such service
equipment enclosures.