Will 2 Generac SE xfer switches work with one set of control wires? N1,N2,T1, 0,194,23

I say yes. Just want to make sure. Never done 2 xfers.

Thanks!
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Will 2 Generac SE xfer switches work with one set of control wires? N1,N2,T1, 0,194,23
No, you can't just parallel the conductors. You need to wire them in a master/slave configuration.

It should be in the genny or ATS instructions; if not, contact Generac.
 