Benton Senior Member Location Louisiana Oct 7, 2011 #1 I had an inspector tell me that I needed two ground rods for a service. Was He just exceeding 250.53 (2) (Supplemental)?
I had an inspector tell me that I needed two ground rods for a service. Was He just exceeding 250.53 (2) (Supplemental)?
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Oct 7, 2011 #2 Unless you meet the exception of 25ohms or less, you need 2.
raider1 Senior Member Staff member Location Logan, Utah Oct 7, 2011 #3 Take a look at 250.56 (2008 NEC) or 250.53(A)(2) (2011 NEC). Chris
W WIMaster Senior Member Location Wisconsin Oct 9, 2011 #4 Check your state codes also. Wisconsin requires 2 ground rods.