Anyone know of code where 2 hour rated cable not required in sprinkler protected areas? Not sure of it is just a NYC code.
Thanks. I asking if you need to run MI cable in an area that is fully protected by sprinklers?I don't quite understand your question, but does this help answer it?
700.10(D)(2) Feeder-Circuit Wiring.
Feeder-circuit wiring shall meet one of the following conditions:
(1) The cable or raceway is installed in spaces or areas that are fully protected by an approved automatic fire protection system.
(2) The cable or raceway is protected by a listed electrical circuit protective system with a minimum 2-hour fire rating.
(3) The cable or raceway is a listed fire-resistive cable system with a minimum 2-hour fire rating.
(4) The cable or raceway is protected by a listed fire-rated assembly that has a minimum fire rating of 2 hours and contains only emergency circuits.
(5) The cable or raceway is encased in a minimum of 50 mm (2 in.) of concrete.
Are you talking about fire alarm cable or feeder cable, as Ron assumed?Thanks. I asking if you need to run MI cable in an area that is fully protected by sprinklers?
Is this at all related to fire alarm? That's where my expertise ends.It's actually low voltage two different circuits.
1. One is control18/2 for a VFD
2. One is power circuit from a panel.