2-hour fire rated pull box, wireway?
anbm
TX
Designer
Does anyone know who make 2-hour fire rated wire way or pull box? Tks
dkidd
here
PE
If you look at UL listing for Metallic Outlet Boxes (QCIT), it seems that any listed metal box can acheive a 2-hour rating when installed in accordance with that listing.
Joe Villani
2 hour rated pullbox
Anbm,
The problem is that as per building code you are limited to a membrane penetration of 16 square inches per opening.
You can always try to get the two hour wall built around (and behind) the box or wireway.
Raider is good with the building code, maybe he will chime in.
Joe Villani
anbm
TX
Designer
I am looking for a wire way/or pull box to be installed in a room without with 2 hour fire rated wall.