A anbm Senior Member Location TX Occupation Designer Nov 4, 2022 #1 If generator room has louvers on some wall portions, how to maintain/meet 2-hour fire rated wall rating requirement at louver portion?
If generator room has louvers on some wall portions, how to maintain/meet 2-hour fire rated wall rating requirement at louver portion?
gadfly56 Senior Member Location New Jersey Occupation Professional Engineer, Fire & Life Safety Nov 4, 2022 #2 anbm said: If generator room has louvers on some wall portions, how to maintain/meet 2-hour fire rated wall rating requirement at louver portion? Click to expand... Install a 2-hour rated fire damper in the wall and install the louver inboard of the fire damper.
anbm said: If generator room has louvers on some wall portions, how to maintain/meet 2-hour fire rated wall rating requirement at louver portion? Click to expand... Install a 2-hour rated fire damper in the wall and install the louver inboard of the fire damper.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 4, 2022 #3 That's the way that we do it. Room is typically built with concrete block and fire rated dampers. We've had large walls that were almost entirely intake dampers.