2 hour rated fire alarm wiring

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
Say you have a 2 story office building and you bringing all of your SLC and IDC circuit directly back to a single FACP on the ground floor, do you need any of your cabling to be 2 hour rated?

Now - what if you put a transponder cabinet on the second floor, such that you are connecting backbone to it with all of your SLC and IDC circuits for the second floor coming off of that secondary panel if you will. Does the backbone need to be 2 hour rated?

Thanks,

Mike
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Say you have a 2 story office building and you bringing all of your SLC and IDC circuit directly back to a single FACP on the ground floor, do you need any of your cabling to be 2 hour rated?

Now - what if you put a transponder cabinet on the second floor, such that you are connecting backbone to it with all of your SLC and IDC circuits for the second floor coming off of that secondary panel if you will. Does the backbone need to be 2 hour rated?

Thanks,

Mike

Do the project specs call for a 2-hour rating?
Are you doing defend-in-place?
Does the building have areas of refuge?
Are you doing partial evacuation?

I may have forgotten one or two, but if the answer to the above questions is "no", then you do not need a 2-hour rated installation. Heck, your cable doesn't even need to be riser rated.
 