I have 480-volt, 3-phase, 50-amp circuit breaker that supplies a 30-amp fused safety switch for a steam boiler and in parallel another 10-amp fused safety switch. The 10-amp fused safety switch feeds a 2-kVA, 1-phase, 480-to-120-volt transformer. The secondary of the transformers feeds a 20-amp fused safety switch that provides power to two small 120-volt loads related to the boiler. I have not treated the 2-kVA transformer as a separately derived system. I have extended the equipment ground from 50-amp 480-volt circuit breaker to the 10-amp fused safety switch, from the safety switch to one side of the transformer secondary, and also to all associated enclosures. I am running a current carrying neutral from the secoudary of the 120-volt transformer and also a non-current carrying ground. Both the neutral and non-current carrying grounds are extended to the 120-volt loads.
Is this arrangement in compliance NEC 2005?