Do I need 2 levels of ground fault for a building covered under 517.40 (nursing home and long term care) or is that just for hospitals.
Also, FWIW, I read 517.17(B) [2011] as describing an additional requirement when GF protection is provided at a high feeder level, but not mandating the presence of higher level protection in the first place. The two sections that do that, 215.15 and 230.95, apply only when the circuit at the upstream point is between 150 and 600V to ground and more than 1000A.The OP is referring to the requirements of 517.7(B). Unless the facility has critical care facilities or life support equipment it would not be needed.