I have an old midwest meter/disconnect pedestal (model m5200c22). Currently has a 200 amp main breaker on the right side and an 40 amp 2 pole on the left side.
200 amp breaker is a g.e. lcb2201 with the 40 amp 2 pole breaker being fed from the lugs off of the 200 amp breaker.
The lugs are on the top (line side) of the breaker.
Would this be considered having 2 main disconnects since the left side 40 amp breaker is being fed from the line side of the 200 amp breaker?
Also need to know the max breaker size that can be installed on the left side when fed from the 200 amp breaker lugs?
Unable to find any info about this meter pedestal.