2 meters for one office

Status
Not open for further replies.
iwire said:
Jim you said you have one transformer feeding this building, the layout is still unclear to me.

However what makes you believe you have two services?

The number of meters or number of disconnects does not determine the number of services the building is fed from.

Read 230.2 carefully paying close attention to the second sentence than take a look at 230.40 Exception 2

Bob,it says one set can supply both.I have 2 sets in seperate conduits.
 
Jim W in Tampa said:
Bob,it says one set can supply both.I have 2 sets in seperate conduits.

Jim what its saying is that more than one set of service conductors from the same source can supply more than one disconnect and it is still ONE SERVICE.

It sounds to me like your building has one service to it.
 